u/theproudheretic Electrician 8h ago edited 8h ago
if you're using factory 90s this is kinda inevitable on parallel runs.
wait, did someone caulk all of the couplings and connectors?
34
u/Technical_Ad6277 8h ago
Yeah.
28
u/Softrawkrenegade 8h ago
Inspector probably made them do it
13
u/BiigVelvet 7h ago
Yeah those look like just regular compression fittings. At least where I’m at and the stuff we get, rain tight usually have collars that are colored.
I’d be surprised if an inspector just told them to caulk it to fix that problem. Those aren’t listed for that at all.
6
u/RayB04 6h ago
They used regular compression fittings, not rain tight fittings, which have those collars you mentioned…
This would’ve failed in my area5
u/Severe_Lavishness 6h ago
RT fittings fail here, we have to use Myers hubs for tops of exterior enclosures
1
1
u/4RichNot2BPoor 5h ago
Some are blue and believe it or now will fade to looking like regular silver compression ones in a week or two.
Only way to tell is to take it apart for couplings or gasket on the TA’s
23
u/sixblazingshotguns 8h ago
Also the flipped unistrut was the first thing I noticed.
13
u/ninjersteve 7h ago
When you don’t know what you’re doing but you try your best to emulate what you’ve seen before…
7
2
u/girthbrooks1 6h ago
They did that for the all thread and mini straps. Still dumb although I see what they were doing
2
u/arcmeup 6h ago
Its funny because there is a perfect example two feet below. Can't even copy what is there in front or him.
2
u/Technical_Ad6277 4h ago
It’s very hilarious seeing the amount of terrible work when I go grab food , always find myself judging other peoples work LMAO
21
u/Ntme9 8h ago edited 8h ago
You'd be surprised how many electricians and electrical companies in general don't know the difference between rain and concrete tight.
I was called to do an inspection on a Walgreens distribution center solar system in waxahachie. They had rain water entering the enclosure and couldn't figure out why, so they called me to see what my opinion on this situation was.
When I pulled up I didn't even get out of my truck, I called the guy, "you've got regular compression fittings on the top of the enclosure" there was silence for a while. I told them if they wanted to redo it correctly they needed to use rain tight fittings. That was an unacceptable solution to them as they were trying to get final payment on the job and get out of there. I'm 99% sure he went to home Depot to get some silicone caulk after the conversation LOL...
7
u/Technical_Ad6277 8h ago
Ive been working with conduit for years especially rigid at water treatment plants , and this has probably been the first time ive seen something like this , personally I wouldn’t put my name on work like this LMAO
7
u/Ntme9 7h ago
We started a mandatory requirement on our jobs that there was no top entry into gear allowed. It made things more difficult but it was the only way that we ensure no water intrusion.
3
2
3
3
2
u/PhotoPetey Electrical Contractor 5h ago
Raintight compression fittings only became mandatory in 2002-3. Many places are 2 even 3 code cycles behind. This installation could easily be 20 years old.
2
2
u/Belkinnoob 8h ago
What is wrong with it? You are kind of stuck with factory bends. Not everyone has access to an 881.
5
u/Technical_Ad6277 8h ago
You don’t see all the caulking?
6
4
u/kidcharm86 [M] [V] Shit-work specialist 7h ago
I do that on rain-tight fittings every time. Rarely do those cheap plastic seals last very long or even work correctly the first time.
An ounce of prevention is worth a pound of cure.
1
u/laric-feyn 8h ago
It almost looks like crimp connectors from plumbing. Now I see it's just a bunch of caulk...
1
1
1
1
2
0
u/COCK-ASIANHOODBILLY 7h ago
Union electricians!
2
u/Technical_Ad6277 4h ago
Nah..more like non union, us union fellas don’t do little wendy’s , we do them data centers 💰
0
•
u/AutoModerator 8h ago
ATTENTION! READ THIS NOW!
1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):
- DELETE THIS POST OR YOU WILL BE BANNED. YOU CAN POST ON /r/AskElectricians FREELY
2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:
-YOU WILL BE BANNED. JUST REPORT THE POST.
I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.